Hello Victron Community and Happy New Year,
I am thinking of updating my Victron setup and adding a second multiplus. At the moment I have a Multiplus 12/3000/120-50 on my system and I am looking at getting an identical one to increase the power so I can run more ac devices. The battery bank is a 12v 702Ah, that contains 16 Lifepo4 Cells. I might be adding an extra 4-8 cells to it in the future.
I am thinking of connecting my battery to a Lynx Distributor and from there connecting the 2 Multiplus and other loads/chargers on my system. Cable lengths will be kept to the minimum and should not exceed 1 meter (battery to lynx and lynx to each Multiplus).
My concern is that as mentioned on the Multiplus manual, the device has to be fused by a Class T fuse and the Lynx is using Mega fuses. I have seen multiple installation where a Class T fuse has not been used, but I am concerned on not following the recommended way.
The next problem I am facing is cable sizing. 2 x 400A = 800A. I need a cable that is large than 120mm2 or 4/0AWG, which is super hard to find and a lot harder to work with.
Has anyone managed to find a solution using a Lynx Distribution system? The system can take the load as it is rated at 1000A, but it cannot take Class T fuses.
I was thinking of adding an 600-800A fuse on the battery side and the connecting to the Lynx Distribution. An alternative could be two cables, each fused with 400A Class T fuse. But then having more fuses on the lynx will increase resistance.
Any ideas or recommendations are welcome.
I am attaching the diagram of my current system for reference.