Does 2 Pylontech 3.55kw Batteries have enough power to run a Multiplus II 48/5000 inverter charger?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Does 2 Pylontech 3.55kw Batteries have enough power to run a Multiplus II 48/5000 inverter charger?
No. The compatibility page recommends 4 but the model is rated for 25A.
While the system will work, you will be discharging them over their continuous amp out rating.
A 5kVA can pull at full rating 83.33A. so you need to make sure at minimum you have a pack that can do that. More if you are starting pumps and you know you may pop over the 4000W
I am assuming you are using the us3000C
Continuous Discharge Rate (Normal Use): 1776 W , so if you have 2 then your max load should never be above 3552W.
The pylontec is also limited in how fast it should also be charged as well.
I dont know how suppliers are on your side, but where we are if they see a mis-sized pack and loads to high for the battery the warranty is void.
This system is only going to be used on weekends and there won't be any more than 3000w being used at once. Does that mean it will be ok?
US3000C is actually rated 37A and 74A peak. 74A and 148A with 2.
Multiplus-ii 5kva can actually draw 93A - 112A at max load depending on battery voltage and around 200A in worst case overload.
3000W on the AC side should work but you would be very close to the limit of the pack but with a peak margin you are probably fine. If you added a third battery you would then be sized correctly and could use the full 5kva.
48 People are following this question.