piemuth asked

115v and 230v as Input for multiplus

Hello,

I will try in english:

We need to use 110v (north-america) and 230v (Most of the world) to feed our 24/3000 Multiplus in our vehicle.

Can I use an Isolation Transformer 3600 (Auto) to use These both voltage without changing any wire for both cases?

I was told this is not working but in the specs I can read, that this transformstor can be just for 115-230 / 115-115 / 230/115 and 230-230V

We only need 115-230 and 230-230....

Or is there any better solution?

Thank you,

Piet


Ps: Second question: what is the different between a Multiplus and a Multigrip for our use in the car?

Multiplus-IIIsolation Tranformer
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Johannes Boonstra (Victron Energy Staff) avatar image
Johannes Boonstra (Victron Energy Staff) answered ·

I was indeed talking about the Isolation Transformator 3600 Auto

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Johannes Boonstra (Victron Energy Staff) avatar image
Johannes Boonstra (Victron Energy Staff) answered ·

The auto-isolation transformer is a good option. You need only to set the board voltage (with a jumper ) during installation and from then the transformer will converter automaticly up/down if it needs to. PS the frequency on board will follow the incoming frequency!

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

piemuth avatar image piemuth commented ·

Johannes, thanks for you answer.

I have to ask: Do you speak from the "Isolation Transformator 3600 Auto"

ITR050362041 ?? That is the product I was thinking from.


or do you mean the "Autotransformator 32A" ITR000100001


I think the "Isolation Transformator 3600 Auto" is the better one....


0 Likes 0 ·