System is including:
- RS 48/6000
- CCGX
- BYD LVS
RS 48/6000 is connected to the CCGX via VE.Direct
Problem: CCGX shows 49% SOC but Inverter shows 98%
Dose anybody know how I should fix this problem?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
System is including:
RS 48/6000 is connected to the CCGX via VE.Direct
Problem: CCGX shows 49% SOC but Inverter shows 98%
Dose anybody know how I should fix this problem?
Hi, the SOC shown on your CCGX in the battery icon comes from the battery itself (via the canbus communication).
Thats the one to rely on.
The SOC in the Inverter RS is calculated by the inverter itself.
That they’re different is not really a problem: the Inverter RS does not use that SOC. Its only shown on the display.
but it is a bit confusing in your type of system, since it now has two SOC values, I’ll see if we can fix that in a future software version.
Inverter RS Product page.
Inverter RS Online Manual.
Inverter RS Datasheet.
Additional resources still need to be added for this topic
Additional resources still need to be added for this topic
48 People are following this question.