AC Coupled Fronius Drops Power on Shifted Frequency Prematurely and More than Needed

Hi, I have an AC-coupled Fronius Symos on 3-phase configured Quattro inverters. I have enabled Frequency shifting in ESS assistant with pre-set configuration: starts at 51, lowest at 52.7, shuts down on 53Hz. I have set the Fronius on MG50 to enable this power reduction on shifted frequency. But lately I noticed that at 80% SOC, the frequency starts shifting up, and the batteries cannot be charged properly on AC PV power, although enough power to charge them fully is available. I also know that Fronius on MG50 starts power decrease at 51Hz and shuts down on 52Hz. What can I do to have better charging for my batteries on AC PV (start frequency shifting on 90% SOC and end with 53Hz on 100% SOC)?

ESSAC PV CouplingFroniusfrequency
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

markus avatar image markus ♦♦ commented ·
Hi,

what battery do you have? CANbus managed Lithium?

BR

0 Likes 0 ·
Nazareth Kevorkian avatar image Nazareth Kevorkian markus ♦♦ commented ·
Rolls 2YS31P. I have a BMV700 as a monitor for the batteries.
0 Likes 0 ·
2 Answers
shaneyake avatar image
shaneyake answered ·

I would change the settings to the settings victron recommends and see if that fixes it.
https://www.victronenergy.com/live/ac_coupling:fronius

50.2 Start
52.7 Minimum
53.0 Disconnect

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Nazareth Kevorkian avatar image Nazareth Kevorkian commented ·

Hi @shaneyake thanks for the reply. Actually I made mistake in the question. It was set just at the recommended settings: 50.2 start, 52.7 minimum, 53 disconnect. BUt it did not function properly and I have undercharged batteries always.

0 Likes 0 ·
Nazareth Kevorkian avatar image
Nazareth Kevorkian answered ·

Update:
I made these changes to the ESS assistant configuration to iterate on results:

Frequencies:

  • Start 50.2 > 50.1
  • Minimum 52.7 > 51.5
  • Disconnect 53.0 > 52.5

What I noticed last 2 days, is that at the Quattro shifts the frequency up to 52.5 at 80% SOC, which reduces the PV output but does not disconnect (Fronius disconnect is at 53Hz). This takeaway is important, because the ESS wants to disconnect the PV power completely to protect the batteries, when the batteries are still at ~80% SOC. This is exactly the scenario I wanted to avoid.

What are the criteria based on which the ESS shifts the frequency: is it the SOC, the Voltage, etc? I would like to be able to do full bulk and absorption up to 90-95% SOC in a pure off-grid Solar scenario and I somehow am not able to control the frequency shifting ESS conditions to enable that.

@Johannes Boonstra (Victron Energy Staff) could you please help me with this issue?

16 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

shaneyake avatar image shaneyake commented ·

On the GX under system settings, is the Battery monitor set to your BMV? Is the Battery Monitor in the Quattro turned off?

0 Likes 0 ·
Nazareth Kevorkian avatar image Nazareth Kevorkian shaneyake commented ·
On CCGX, the battery monitor is on Automatic and it has been always auto-selected on BMV700 on VE.Direct.

In VE.Config settings pushed into the Quattros, under General tab page, the battery monitor is selected. Shall I deselect it?

0 Likes 0 ·
shaneyake avatar image shaneyake Nazareth Kevorkian commented ·

I would set the Battery monitor to BMV700, auto doesn't always work.


From my understanding, if you are using a external Battery Monitor you should uncheck the VE.Config Battery monitor.

0 Likes 0 ·
Nazareth Kevorkian avatar image Nazareth Kevorkian shaneyake commented ·
Done. But do you believe that this is the problem? I believe that the problem is elsewhere, because w/o changing these settings with just ESS frequency settings change the behavior changed.
0 Likes 0 ·
shaneyake avatar image shaneyake Nazareth Kevorkian commented ·

If the Quattro isn't getting the correct battery information it will frequency shift incorrectly.

So in mind, what you are saying is that the system is reducing the charging too early makes me believe the system doesn't know the correct state of the battery is. Let's see what these settings do.

Is the ESS settings still?
50.2 Start
52.7 Minimum
53.0 Disconnect

0 Likes 0 ·
Nazareth Kevorkian avatar image Nazareth Kevorkian shaneyake commented ·
It is now.
0 Likes 0 ·
shaneyake avatar image shaneyake Nazareth Kevorkian commented ·

Is everything working now?
Can you post some screenshots of SOC and Frequency?

0 Likes 0 ·
Nazareth Kevorkian avatar image Nazareth Kevorkian shaneyake commented ·
Now we are at night and we happen to have grid AC in. We shall wait until tmrw day time.