question

ehsab avatar image
ehsab asked

Quattro and Inverter RS in the same system?

Hi,

I was wondering if it is possible/supported to run both quattro and Inverter RS together with a GX device and a batterybank?

Kind Regards
ehsab

inverter rs
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@ehsab

No not supported.

Yes you can sort of run both off the one bank, if your bank can handle the amps for both inverters at 100% / overload. Soc will be all over the place and difficult to track. I am not recommending that either. There are many other considerations.

As for sharing the gx since they are both ve bus. No. As you cannot program them as a parallel system. You need the same units for that application.

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ehsab avatar image ehsab commented ·
Hi Alexandra and thanks for taking the time to reply.

I have a Lynx Shunt that measures in and out of batterbank, and a well sized batterybank aswell.
What other considerations do you mean?

Could I not use the VE.Can bus to connect the Inverter RS Smart Solar to the current system?

I'm not seeking to parallel the units, just add an inverter for a backup solution to the quattro.
The MPPT is just a bonus i will use later when i have more solarpanels.

0 Likes 0 ·
shaneyake avatar image shaneyake commented ·
The RS inverter does not have VE.Bus, only VE.CAN and VE.Direct.


I haven't tried a RS and VE.Bus inverter on the same GX yet, but I have tried to get the GX to see multiple Inverters with no success. But It may show up using the VE.Direct port. From what I can tell the software just doesn't know what to do with 2 inverters connected.

Are you batteries CAN? if they are then you can connect 1 bank to 2 GX's.
From what I have seen the GX's don't transmit on the Battery CAN port.
You could then have a GX for each system.

I am not sure about the Lynx Shunt, it may or may not work with 2 GX's

0 Likes 0 ·
ehsab avatar image ehsab shaneyake commented ·

I'm not using a BMS if that's what you mean, i have lead batteries connected to a Lynx Shunt (which is VE.Can connected).

@Alexandra any thoughts on this topic now that you have a little more info.

0 Likes 0 ·
Show more comments

Related Resources


Inverter RS Product page.

Inverter RS Online Manual.

Inverter RS Datasheet.

Additional resources still need to be added for this topic