I got a 3P Multiplus 48/5000 installation running, with 10kw Solar and ~45kwh LiFe4Po Battery storage. The PV Inverter is an Fronius Symo 10.0-3-M.
This setup has been running totally fine for the last ~2 years.
Now... it's happening EVERY morning, that the solar inverter is no longer present on the main tab, but it still is in the menu. CCGX and Fronius are hard-wired, network settings haven't been touched - but of course, both are in the same network, (192.168.0.xxx / 255.255.255.0).
The CCGX does indeed 'see' the fronius, the IP address is detected and fine, but in the device list the fronius appears as "not connected", and if I enter its device parameters, it appears as "connected unknown".
As soon as I restart the CCGX (every morning) all is fine and the whole setup is running like a charm until the Fronius looses DC power (sunset). The next morning the above mentioned is happening again.... groundhog day^^.
Any clues?!
Grtz,