question

sven-1 avatar image
sven-1 asked

VRM dashboard numbers don't add up

1628613841833.png

From this screen shot, the inputs and outputs do not even closely add up. The house is consuming 9kW, the solar is hardly generating, the battery is charging although at -5.5kW, and the grid meter is showing feeding back to the grid at 1.6kW.

This is a 3-phase installation with 3 5kVA multiplus II, one per phase.

Phase rotation maybe?


VRM
1628613841833.png (51.6 KiB)
4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

shaneyake avatar image shaneyake commented ·

What kind of meter are you using? Possibly the CT is backwards on L2? If L2 is reversed the numbers mostly add up within some margin.
The battery is discharging in this screenshot, the label may not have switched yet.

0 Likes 0 ·
sven-1 avatar image sven-1 shaneyake commented ·
ET340 3-phase meter is used.

Even when ignoring the label on the battery the numbers still don't add up.

0 Likes 0 ·
Show more comments
2 Answers
sven-1 avatar image
sven-1 answered ·

We actually figured it out, it was a phase rotation issue, which we resolved by swapping phase 2 and 3 between the main incomer and the grid meter, then reversing this for the 3-phase circuit breakers for the pumps. All sorted thank you.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Willem avatar image
Willem answered ·

1690130011638.png


These also dont add up


103-12-22 =69 Watt difference during the day with PV available even bigger diference's are experianced


Multiplus II 5 KVA , Cerbo GX , ET112 , Freedom Won e-tower bateries(2)


what can be the reason ?


1690130011638.png (74.5 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.