Multiplus ii 2x 120 Mounting in Propane Tank Compartment

Any issue mounting the Multiplus II or MMPT solar charge controller in the same RV compartment as the propane tanks?

Multiplus-II
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
z69 avatar image
z69 answered ·

As the Multiplus ii and i presume the MMPTT charge controllers are NOT rated to be installed hazardous locations, i will NOT install any equipment that is not safe to install in that location.
Equipment has to be rated Gas Group(ATEX, IEC or NEC 505) IIA.
Propane falls under Gas Group IIA.
You only need 1.7% propane in the air to cause an explosion.