ESS - Mode 3 (External Control) SetPoint wont accept negative number

Hi Guys,


Trying to manually control a Quattro with Cerbo GX via ModBus.

I have followed the ESS mode 2 & 3 documentation.


When ESS mode 3 (external control) is active, the SetPoint wont accept a negative number.

See screen shot to see Charger and Feed-In address status.


Has anyone come across this before?


I have tried -1, -10, -100, -1000 I just get the error as attached. Positive numbers are accepted without issue.



Thanks in advance!


1628050358145.png

Modbus TCPmodificationsess grid setpoint not reached
1628050358145.png (13.6 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
juan manuel tirado avatar image
juan manuel tirado answered ·

In case someone would like to know, I have already figured out how to write negative values via ModbusTCP in the CCGX in register 2700 of the Register List. This specific register is int16 and admits values between -32768 and 32768, but .... to write negative values you have to send 65536 minus the absolute value to send. Example: if I want to write -50W in the GridSetPoint, via modbustcp I would have to write 65536-50, I mean, 65486.


Por si a alguien le viene bien saberlo, Ya he averiguado como escribir valoras negativos via ModbusTCP en la CCGX en el registro 2700 del Register List.

Este registro concreto es int16 y admite valores entre -32768 y 32768, pero....para escribir valores negativos hay que enviar 65536 menos el valor a enviar absoluto.

Ejemplo: si quiero escribir -50W en el GridSetPoint, via modbustcp tendria que escribir 65536-50, osea, 65486.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Mark avatar image
Mark answered ·

Maybe check if you are currently sending a string or number to the Modbus node, if it's not already a number try converting the msg to a number before sending it through.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

tenacioustech avatar image tenacioustech commented ·

Thanks for the reply, yes the data is being sent as a number/integer already.


1628078148488.png

0 Likes 0 ·
1628078148488.png (5.7 KiB)
tenacioustech avatar image
tenacioustech answered ·

Can anyone let me know what Register and Unit ID they're pushing a negative integer to when using a Cerbo GX? (Note the documentation doesnt list a Unit ID to write to for Cerbo GX)

Thanks

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Mark avatar image Mark ♦♦ commented ·

Look under 'Services' > 'Modbus TCP', the unit ID should be 100. According to the Modbus list, the register for 'ESS power setpoint phase 1' is 37. Sorry I don't have an ESS system available to test this specifically.

0 Likes 0 ·