Installation suggestions ESS DC PV

Can somebody explain the difference of installation suggestions ESS DC PV at page 6 in this manual https://www.victronenergy.no/upload/documents/MultiPlus-II-to-MultiGrid-and-MultiPlus-comparison-EN.pdf ? Advantages and disadvantages?

Multiplus-IIinstallation
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
boekel avatar image
boekel answered ·

one uses an external current sensor, using this you don't have to wire all users through the Multi. It can safe re-wiring of your system.

(note that when installing Multi further from grid-panel you cannot use extension wires for the sensor, and you'll have to use an energy meter wired to Venus instead).

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jeibre avatar image jeibre commented ·

Thank you!