question

kallenr avatar image
kallenr asked

EM24 or ET340 -> ESS on 3phase grid, 1x Multiplus 2, Belgium (slimme meter)

Which is the best meter for the Belgian market in Flanders?

- 3 phase grid
- 1x Multiplus 2 5000W
- 1x Cerbo GX
- 1x Cerbo touch 50 (because it can)
- 1x ET112 (for monitoring solar panels, mono phase inverter)
- EM24 or ET340 ? (net monitoring)


I am talking about the 3 phase "smart meters".
I definitely want to use phase compensation!
So the sum of the consumers of the 3 phases must be fed back over 1 phase to the grid.
(which the Multiplus 2 is connected to)

Which meter is the most suitable? (EM24 or ET340)

Fluvius meter: 3 fase / Sagemcom - Siconia T211
20210724-163935.jpg

ESS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

In a system with 3-phase grid and only 1-phase ESS you should use an EM24.
With the ET340 you would get visualization errors (but the system would work as good as with the EM24).

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

frederikbove avatar image
frederikbove answered ·

I’m also living in Belgium and have the same setup with an em24 and it works perfect

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kallenr avatar image
kallenr answered ·

@Matthias Lange - DE & @frederikbove thanks for the input!
i did order the EM24 and ET112 for monitoring my mono phase Solar array.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

laulau avatar image
laulau answered ·

I have the same setup in Belgium. but have used an et340 as grid and an et112 for the pv. the data on vrm are not correct in any way. would this be solved with an em24?

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

laulau avatar image laulau commented ·

the problem has been solved by placing an EM24

0 Likes 0 ·
kallenr avatar image kallenr laulau commented ·

@LauLau thanks for your follow up!

0 Likes 0 ·