Hi I have a Quattro that I have just replaced the Failing AGM battries with 4 24v 100Ah batteries wired in parallel and changed all settings as per Victron specs the problem in having is when the batteries are full the Quattro is completly shutting down and restarting without any alarm.
my observations are that the dc voltage starts to climb and when it gets to approx 30v it faults out, I,m wondering if the bms in the batteries is disconecting causing the spike in voltage causing the inverter to trip.
if so is there a work arround for this? the batteries are standalone not connected to the inverter, im using the standard Victron LifePo settings which is lower then the batterys recomended im pulling my hair out here any help would be appreciated thanks.
Ok I disabled the charger in the Quattro and am charging off the solar and is cutting off as it should and not spiking the voltage the problem is the quattro pushing the voltage up to 30v then tripping any ideas?