question

James Demetriou avatar image
James Demetriou asked

Shore power limit on MultiPlus Compact 12/2000/80-50 120V keeps setting itself to 8.5 Amps

The MultiPlus 12/2000/80-50 has a minimum shore power limit of - 4.5A according to minimum shore current limits 07-2019.xls which I downloaded from victron. When I set the CCGX to 4.5 and exit the menu, the value pops back up to 8.5A. Why might this be happening and how can I get it to 4.5Amps? I also tried to set it via a bluetooth smart dongle. Same behavior.

Could it be that the rating/spreadsheet is not for North America at 120 Volts and only 4.5A for 220V? That would really be disappointing and should probably be mentioned on the spreadsheet. Also I can't turn off power boost, I need it.


Thanks!


James


current limitshorepower
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
JohnC avatar image
JohnC answered ·

Hi @James Demetriou

I think you may be misreading that spreadsheet. Your unit is listed under ID 2708 (27 means 120V) at 8.4A.

1626941067024.png



1626941067024.png (60.9 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

harold avatar image
harold answered ·

I think your setting (in VE config) does noet allow manual changing in the CCGX.
You need to change your settings.

(I have the generator fixed and the shore power amps manually changing allowed)

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

James Demetriou avatar image James Demetriou commented ·
Thank you for pointing out the proper line item on the spreadsheet.
0 Likes 0 ·

Related Resources