question

cottersay avatar image
cottersay asked

Phoenix 500VA 12V-120V shutting down with 150W laptop transformer!!!


I have the Victron Phoenix 12V/500VA 120V AC Pure Sine Wave Inverter (as well as other Victron inverters), and I run into a problem when I try to power/recharge my HP Pavilion laptop off of it: The 12/500 (as well as my other Victrons) immediately shuts down (LEDs indicating overload or short circuit). There are no other loads on the inverter when I do this, either. However, the laptop does not have this issue when plugged into the 120V mains or a 300W Solar Generator.
(The HP's power supply is a basic 150W HP power brick.)
How can I prevent this from happening? Any thoughts?

Thank you!

-C. W. Sayre
Phoenix Inverter
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

wkirby avatar image wkirby ♦♦ commented ·
Yes, those HP laptop chargers are a nightmare. The inrush current on them is too high.

I have two of them for my work laptops, I cannot have them on the same circuit otherwise they will drop a 16A circuit breaker when switched on.

1 Like 1 ·
cottersay avatar image cottersay wkirby ♦♦ commented ·
Thanks -- I thought that was the problem!
0 Likes 0 ·
1 Answer
cottersay avatar image
cottersay answered ·

Victron, for all intents and purposes, has no Customer Support, and this useless forum is certainly no substitute.

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

klim8skeptic avatar image klim8skeptic ♦ commented ·

Going back to your Previous Question , where have you wired the inverter to?

0 Likes 0 ·
Show more comments