question

dii11012 avatar image
dii11012 asked

BMV 700 and Solar

Recently had solar installed to RV. I think they bypassed my BMV 700 by connecting negative cable from solar directly to battery negative (see photo). Is solution to move the negative from solar to the load side of shunt (bottom lug)? Thanks for advice.


shunt.jpg

BMV Battery Monitor
shunt.jpg (2.0 MiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
wkirby avatar image
wkirby answered ·

Absolutely correct. The solar charger negative needs to move to the load side of the shunt in order to count the energy into the battery.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

dii11012 avatar image dii11012 commented ·