I have an issue with a Victron multiplus connected to an SMA SB5000TL-10 on a Remote power system setup - No grid power to site.
The Victron inverter is driving the frequency up to 52 Hz and shutting down the SMA inverter as it should at full battery charge but it is not lowering the frequency back to 50Hz when there is a load on the system and SOC is dropping.
If you drop power to the Muliplus and restart after a 20 minute delay, It starts up again with 50Hz and the SB inverter starts supplying power and charges the batteries.
Happy to be corrected but the SB5000TL settings are E0 for off grid, Unless Ive missed something here.
Ive changed the settings in the grid control on the Multiplus to 51Hz start control to 52HZ shut down the feed from the SMA.
Not sure where to go but will probably start afresh / go back to default settings and start over again with the Victron but if any one has some pointers this would be very much appreciated.
Secondly, im of the understanding that unlike SMA sunny islands, the Victron inverters need a DC coupled bank of solar modules to stop 'lock out' where the Victron shuts down and wont restart at all unless the battery voltage is increased via and alternative source. Any thought on this?