question

dmay avatar image
dmay asked

AH setting

I just installed my BMV -712 smart. I have 4 - 6v in series with 235 AH in each. I set the unit to 470 AH and it took it but on the main readout it is reading 240 AH only. I tried to reset but it still shows 240. Doesn't seem right!

BMV Battery Monitor
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Kevin Windrem avatar image Kevin Windrem commented ·

470 seems correct for 2s2p configuration.

What are you calling "main readout"? And where are you setting the value?


0 Likes 0 ·
2 Answers
Stefanie (Victron Energy Staff) avatar image
Stefanie (Victron Energy Staff) answered ·

Hi @Dmay,

4x 6V/235Ah in series = 24V/235Ah

If you put them all in parallel, you'll get 6V/940Ah (Thanks for doing the correct math, Mark)

If you put them in series/parallel (2s2p), you'll get 12V/470Ah.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Mark avatar image Mark ♦♦ commented ·
4x235Ah in parallel is 940Ah, not 470Ah :-)

Not that you would actually wire it that way, as it's only 6V...

0 Likes 0 ·
Show more comments
dmay avatar image
dmay answered ·

Yes they are series/parallel.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources

Additional resources still need to be added for this topic