Having issues with a system that I installed for a customer recently that I simply cannot figure out. The smartsolar 150/70 provided full production the first 24 hours that it was installed. In subsequent days, solar production dropped (day 1 = 590wh, day 4 = 20wh). Location remained pretty much constant, with roughly equal sun each day.
At the same time, battery voltage/state of charge was gradually going DOWN, according to the smartshunt. This confirmed that the smartsolar was not producing PV power, while power was being consumed from the battery bank. During this same time, there was a widening discrepancy between the battery voltage being read by the smart shunt and the battery voltage being read by the charge controller. At one point, the solar controller read 13.49v vs. smartshunt 13.10v. A day later, the solar controller read 13.49 while the smartshunt read 11.95v (at the same time the smartshunt read 100% state of charge, which made no sense).
Pretty lost here - I'm not on site anymore, which complicates the troubleshooting, but would love any suggestions. I verified that settings were correct after installing everything in the system.