question

trougnouf avatar image
trougnouf asked

Will a turned off GX cause the VE.Direct BlueSolar MPPT to turn off?

The GX device is supposed to get its power from the VE.Bus BMS' load disconnect pin per the manual.

The GX device controls the BlueSolar MPPT through VE.Direct.

In case of depleted batteries, will the GX off state default to letting the MPPT charge or not?

MPPT Controllersgx device
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
wkirby avatar image
wkirby answered ·

If communication to the GX device fails then the the MPPT will fall back to its internal charge settings. Make sure that the MPPT is set up for your batteries so that they continue to be charged correctly in the event of a communications failure.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

trougnouf avatar image trougnouf commented ·
Wonderful, thank you! :)
0 Likes 0 ·

Related Resources

MPPT Product Page

MPPT Error codes

MPPT 150/60 up to 250/70 Manual

Additional resources still need to be added for this topic