Multigrid RESU 6.5 charge current seems to be limited

Now as I have more PV power added to my multigrid, the charge current going into the battery seems to be limited @25A max. This leads to power being fed back into the grid, what I don't want to do. Is this maybe a battery limitation managed by the RESU itself ?

Grid setpoint is 30W

Charge power setting is "not limited".

.....

Just found the setting in the assistant - 26A. Datasheet says 37.8A max !?

Now my question is ...can I simply increase this ? Any hint or even experience ?

Txs

multigrid
1551007583623.png (808.6 KiB)
1551007628444.png (26.3 KiB)
1551007832612.png (29.6 KiB)
1551007863828.png (27.2 KiB)
1551008903982.png (124.0 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

You can increase that charge current value in VEConfigure.

Presuming all other values are set correctly, the system will limit the charge current dynamically (if necessary) from information it gets from the battery via the CAN-bus.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

vicky avatar image vicky commented ·

Thanks a lot !