I've never had this problem until recently but I've been unable to set a current limit, and I am seeing the following error that I do not understand. My setup hasn't changed so I don't understand why this no longer works.
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
I've never had this problem until recently but I've been unable to set a current limit, and I am seeing the following error that I do not understand. My setup hasn't changed so I don't understand why this no longer works.
This is the setting it's asking you about - "overruled by remote" - are you able to check that it's enabled?
Did you update firmware recently? When updating the firmware all settings get reset, I'm not sure what the default option is.
MultiPlus Product page / Quattro Product page
MultiPlus 230V Manual / Quattro 230V Manual
MultiPlus 230V Datasheet / Quattro 230V Datasheet
VE.Bus Error codes / VE.Bus configuration guide