question

andrer avatar image
andrer asked

Fuse for Battery negative pole in case of lightning impact

Dears, this is my current, well running setup:

EasySolar 5kW + 48V 10KW Lithium Battery (Winston-cells) + 480W Solar Panels

Installed in a cabin, 2000m elevation in the alps -> So its a "island system" with no access to a grid

The cabin is protected against lightning impacts with a lightning rod. Unfortunately, the resistance is a little high with about 100 Ohm.

The EasySolar ground is connected to the lightning rod in order to be grounded.

I worry a little bit, that a lightning impact might damage the electronics, due to the high resistance in to the ground. I have installed fuses to protect everything as good as possible. Only the battery negative pole is directly connected to the EasySolar.

Question 1: Should I install a fuse on the negative pole of the battery as well? Because in case of a impact, the lightning would go into the rod and therefore directly to the earth connector of the EasySolar and then through the negative pole into the battery (if the resistance is lower than 100 Ohm).

Question 2: Would it make more sense, to unhook the system from the lightning rod and give it its own grounding? -> In case of a impact (in to the rod), the only connection would be through the solar panels which have a decent fuse.


Many thanks for your advise!

Lithium BatteryEasySolar All-in-Onefuses
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Mike Dorsett avatar image
Mike Dorsett answered ·

You should certainly keep the Lightning ground separate from all other ground connections. Giving the Multiplus it's own ground would be best practice. Personally I don't see fusing the negative pole of the battery to be any advantage. A direct strike is going to cause a lot of damage, however systems are earthed. Being in the mountains, you probably have thin soil over rock, which gives the high ground resistance. I would look at trying to create a ground grid for the lightning protection to lower the ground resistance. If you can do this successfully, then connecting the Multi plus system to this grid at one point only would be acceptable. The concept would be like turning the house into a Faraday cage, with all the electronics inside. This will include multiple grounds, a lot of heavy bonding straps using copper bar, and multiple lightning spikes to discharge the local field. I used to have a steel Sailing yacht with a 22m Aluminum mast. In 11 years, we had 4 close strikes - some which upset the electronics and compass. We never had a direct hit as the mast & shrouds gave a cone of protection. We only had one instance where one piece of electronics was actually destroyed by the discharge.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

andrer avatar image andrer commented ·
Dear miked, giving the MultiPlus its own ground was also my thought... But if I understand you correct you are saying, that if I can achieve a much lower ground resistance, it would be OK to hook the MultiPlus to it, but only on one point? Like from the MultiPlus "earth screw" directly to the rod? Sorry for asking, but the more I know the less I know ;-)
0 Likes 0 ·
Phil Gavin avatar image
Phil Gavin answered ·

When you say this:

"The cabin is protected against lightning impacts with a lightning rod. Unfortunately, the resistance is a little high with about 100 Ohm."

My question is: A 100 Ohm resistance between the lightning rod and where?

I assume that is to somewhere else that you deem to be at earth potential.

Multiple earth spikes that are not directly connected will result in problems, not solve them.

Different earth spikes for different parts of the same building could be very dangerous during a lightning strike. They will develop high voltages between them as the lightning dissipates charge in the ground.

For a decent earth connection, you can use multiple localised electrically connected spikes to increase contact area. Pick your dampest ground and adding some salt will also help. But then everything goes back to that same earth.

If your property is surrounded by a metal fence make sure that is connected to the same earth, (on both sides of any gates).

Things that are likely to get hit, should go directly to the earth on an independent cable by the shortest route. Minimize bends and don't have loops in any earth cable.

Put a ferrite core around both positive and negative (together) of PV cable pairs coming from the roof. This will give your PV DC cables a high surge impedance and the discharge may choose an alternative route.

No fuse will provide lightning protection. It is too slow, and lightning has breached the air gap to the clouds, so another inch won't present a problem.

I think convention surge protection is probably too slow as well, but it won't hurt. I'd use them in conjunction with Transil diodes.

Use Transil diodes: battery positive to earth, battery negative to earth and positive to negative. Transil diodes have the fastest avalanche response I know of, and may offer some protection by diverting current to earth.

There will still be no guarantee.



2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

andrer avatar image andrer commented ·

Thank you Phil!!!

100Ohm: I wrapped this measuring device (borrowed from a friend) around the rod and measured: https://ch.rs-online.com/web/p/erdungsprufgerate/1365146/ There is not a lot you can set up on the device. He said, that 100 is way to high for regular buildings, but a possible value in the mountains. It probably prevents the house from catching fire.

But anyways, so your advice is to keep the inverter's earth hooked to the rod but adding surge protection and Transil diodes between rod and system-earh? or between system (EasySolar) and battery? And also add ferrit cores to the solar-DC cable.


0 Likes 0 ·
Phil Gavin avatar image Phil Gavin andrer commented ·

All earth points should be equipotential, in other words, all earth points should be decently cabled together.

Any and all surge protection to earth should be connected at one side to this one electrical earth.

You should try and improve upon that earth spike measurement using the methods I suggested. This is important.





0 Likes 0 ·