question

matt23 avatar image
matt23 asked

inverter off

I have a "3 phase" system running off 3 inverters, they charge the batteries from a generator. When I try charge from the generator the device says OFF but I can see the SOC and voltage both of which are fine. I also checked the gen voltage which is also fine. When I switch to charge only the CCGX the switches to fault.


Anyone know what this could be?

MultiPlus Quattro Inverter ChargerGeneratorfault
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

klim8skeptic avatar image klim8skeptic ♦ commented ·
Could you please post screenshots relating to your problems?
0 Likes 0 ·
matt23 avatar image matt23 klim8skeptic ♦ commented ·

as you can see the inverter is switched on but not doing anything20210616-112012.jpg20210616-111915.jpg

0 Likes 0 ·
1 Answer
Mike Dorsett avatar image
Mike Dorsett answered ·

Have you checked the phase rotation of the generator compared with the system? If the Generator rotation is 'backwards' it would show a fault.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

matt23 avatar image matt23 commented ·
Yes the phase rotation is correct and I can test at the inverter AC to see the the power is getting to the inverter. it clicks in and out every now and then but never charges