question

northernboy avatar image
northernboy asked

Grid and new Generator have different Phase Sequence, how to correct?

My 3 Phase Grid sequence is (According to the grid meter on the color controller) L1-L3-L2

screenshot-2021-06-09-at-155434.png


I just connected my new generator and with the....


Multiplus's switched to "on" Inverter lights on constant. No Battery Charging.

Multiplus's switched to "charger only" main lights flash on line 1,2, main and float lights flash on line 3, No Battery Charging.


I then checked my 3 phase Generator sequence and (According to the grid meter on the color controller) it's L1-L2-L3


What is the best way to fix this issue, I guess the system is set up for L1-L3-L2 as it all works fine when the grid is connected.

Generator
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

harold avatar image harold commented ·

Just can switch 2 connections of the generator, i suppose???

0 Likes 0 ·
northernboy avatar image northernboy harold commented ·

I did wonder if I could just switch L2 and L3 on the Genset plug wiring but thought I would ask first.

0 Likes 0 ·
2 Answers
northernboy avatar image
northernboy answered ·

I am answering my own question in case someone has the same issue. I switched L2 and L3 over on Genset, now Genset and Grid have same phase sequence. Everything now works OK.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ted avatar image
ted answered ·

I have the same problem. So you did only switch the L2 and L3 at the IN and OUT Port from the EM24, or?

12 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

wkirby avatar image wkirby ♦♦ commented ·

As he says above, he switched L2 and L3 on the generator.

0 Likes 0 ·
marekp avatar image marekp commented ·
@Ted

Switch L2 & L3 only at the EM24 input.

0 Likes 0 ·
ted avatar image ted marekp commented ·

I have a 3 phase Multiplus System. Think, if I only change the EM24 Input Port, then a phase rotation error would appear in the MP System, since you set each Multiplus to a specific phase in the VE Configurator

0 Likes 0 ·
marekp avatar image marekp ted commented ·
@Ted

The error you see is caused by the difference in phase rotation between incoming AC and your Multiplus system.

You have 2 options.

1. change phase rotation on the input of your system (EM24).

2. change phase rotation of your Multiplus system.

First option is simpler and does not require changing phase rotation on all your 3 phase loads.

0 Likes 0 ·
ted avatar image ted marekp commented ·

"The error you see is caused by the difference in phase rotation between incoming AC and your Multiplus system. "


To clarify. The L1-L3-L2 Phase sequence in the Cerbo EM24 overview currently throws NO phase rotation Exception in the MP system at all. With an additional 3-phase generator at the AC-In, it is another thing.

I can of course change L3-L2 already at the output of the main switch for the AC-IN of the MP System. But still not sure, that I then need not reconfigure the MP-2 and MP-3 with the configurator since they get another phase. But the MP has each a phase detection, like the EM24. So, is it possible that the EM24 "rewires" the L3-L2 already?

0 Likes 0 ·
marekp avatar image marekp ted commented ·
@Ted

Change the EM24 input AC phase rotation and see what happens. :)

0 Likes 0 ·