VRM math problem

I have a math problem reading a VRM numbers.

See for yourself.

screen-shot-2021-06-04-at-102132-pm.png

Total consumption = 1353W

Grid = 20W

From battery = 677W x 0.90 = 609W (90% inv eff)

So VRM math is as follows.

1353 = 20 + 609 ?

Same here.

(this pict was removed to simplify the problem)

Any comments?

Where is the problem?

VRM
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Phil Gavin avatar image
Phil Gavin answered ·

Grid CT reversal?

6 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

marekp avatar image marekp commented ·

There is no CT.

Grid is measured by EM24 power meter in the first pict.

I will remove the second pict because it is confusing the problem because it shows intermittent behavior when inverter/charger is used as grid power meter.

0 Likes 0 ·
markus avatar image markus ♦♦ marekp commented ·

Hi Marek,

I am pretty sure your EM24 is miswired.
BR

0 Likes 0 ·
marekp avatar image marekp markus ♦♦ commented ·

There are only 3 input wires and 3 output wires.

How one can miswire this?

0 Likes 0 ·
Show more comments
marekp avatar image
marekp answered ·

Just to update.

There was a simple reason for the wrong numbers.

Problem was fixed by swapping phases L1 and L3 on the LM24 power meter.

Below the numbers after fixing this problem.

screen-shot-2021-06-05-at-92850-pm.png

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Phil Gavin avatar image Phil Gavin commented ·

Thanks, for the report back, I thought those grid meter readings looked dodgy.

0 Likes 0 ·
Murray van Graan avatar image
Murray van Graan answered ·

Which batteries are you using? In both instances, the battery discharge rate is roughly half the load?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

marekp avatar image marekp commented ·

Winstons (LFP) with "2 signal BMS" in both, but lets concentrate on the top one only.

0 Likes 0 ·