Another Inverter Overload with ESS question

For some time I've noticed my inverter give overload warnings. On investigation I found that if my load exceeds the inverter capacity, let's say 5000W then I have an overload warning even when the grid is connected and solar producing power.

My configuration is:

Grid Connected

Quattro 5K, 481

RS450/100 producing +-3000W

Load +-5000W

Battery supply remaining +-2000W

Grid supplying some watts, minor values though.

Both ACOut1 and ACOut2 in use as per normal No Grid Failure scenario.


Why would the inverter give an overload warning when it's maxed out on Inverter power but the connected grid is still connected to provide 'top-up' when needed?

We all know the inverter is at max so while the grid is connected I don't really care. When the grid is NOT connected then YES, then I need to know about it. Can that setting not be amended to not warn me on a daily basis that my inverter is working hard for it's money?


Ingo

MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Alexandra avatar image
Alexandra answered ·

@Ingo

A warning is just that. You know you are pulling more than the inverter can invert. It is a warning and in the even of grid faliure it will become an alarm.

The inverter will be trying to carry the whole load if you have set the grid set point down as well and be trying to power assist so working hard.

Have you set the max inverter power in the ess menu? on a 5kva set it to around 4000 or alower if you are in a hotter area. I have seen is make a difference in any case to the warnings. Still get them though.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Ingo avatar image Ingo commented ·

Thanks @Alexandra I thought of setting the limiter to 4000 but then decided against it. My thinking is: Let the inverter run full taps, it's built for that and why hamstrung the unit down to a smaller value.

The warnings, while grid-connected, just seems pointless to me in this situation as I am not going to lower the load on the inverter. If it needs more power it will just import power from the grid - which I am fine with.

0 Likes 0 ·
marv21 avatar image
marv21 answered ·

"The warnings, while grid-connected, just seems pointless to me in this situation as I am not going to lower the load on the inverter. If it needs more power it will just import power from the grid - which I am fine with. "

Thats my thinking too. Iam in the same Situation. Getting spammed with "Overload" Warnings. Its annoying that the Inverter themselfs drive themself that hard to get this Warning. I now just disabled it the Warning. Somewhere I can understand that a Warning is not an Alarm, but ON-Grid its just useless to have it, if there is no Danger ahead.

13 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ejrossouw avatar image ejrossouw commented ·
Are you using ACOUT for loads? Do you require an essential load function?
0 Likes 0 ·
Ingo avatar image Ingo ejrossouw commented ·
@ejrossouw I don't know about @Marv21 but I use ACOut2 for heavy loads and ACOut1 for Critical loads. When the grid/solar is connected it supplies power to both which is 100% in line with the design of the unit.
0 Likes 0 ·
marv21 avatar image marv21 ejrossouw commented ·

I have everything connected to ACOut1.

Therefor in an Offgrid Situation i have to care not to switch on to many heavy loads.

I see the Warnings more like a "Hey, care. If you switch to off-grid now (Power outage) then i will shutdown." now. But i shut them off.


0 Likes 0 ·
shaneyake avatar image shaneyake commented ·

I like having the warnings because it is letting you know that the inverter is limiting because it is getting too hot. If you increase the cooling or lower ambient temperatures you can get a few more watts out of the inverter. Warning is just there to say hey, I had to reduce power because things were getting hot. You can see the warnings on VRM without getting notified.

0 Likes 0 ·
Ingo avatar image Ingo shaneyake commented ·
It's the middle of winter here and the temperature of the inverter is around 10 degrees C.

I think the issue is not very clear. The Inverter is connected to the Grid, it's not overheating and there is nothing wrong with pulling say 10KW from a 5KW inverter when connected to the grid - it's designed to do that.

Why would I then get an Overload Warning if the grid supplies 5.5KW and the inverter 4.5KW? Or better yet, Max from Inverter and the remaining from the Grid. If I increase load to 15KW then the Grid just supplies more, the Inverter stays at Max power as designed - it should whine about it unless it's connected to Battery only..

0 Likes 0 ·
Show more comments
marv21 avatar image marv21 shaneyake commented ·
Yep here is summer, but the Inverter is around 19°C. I think it is not to hot. The Warnings appear as soon as i heavy load is switched on. In my Opinion the Warning should only accour if the Shutdown of the Inverter (Alarm) is close ahead. But i can have a warning for hours. It will never Shutdown. On the other Hand i can see the upside of that. If you get a Warning it means "Hey, care. If you switch to off-grid now (Power outage) then i will shutdown."



0 Likes 0 ·
Show more comments
dcsonka avatar image
dcsonka answered ·

Hi,

I wrote a doc on my experience with similar issues. See attached.

Limit inverter power.pdf


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.