question

sheakx avatar image
sheakx asked

Proper Smartshunt Connection

I have 2 100AH lithium batteries on a boat where the negative is parallel jumpered at the batteries with a single negative wire going to the load. The 2 positive terminals run independently to a battery switch about 6 feet away. 99+% of the time, the battery switch is set to use both batteries and the load draws from both. This has never been a issue. Can I just treat this parallel bank as a single battery? From reading other posts, it seems like the long leads to the battery switch may not be a good idea. This was the factory set up and I can’t see a great benefit in trying to manually manage these 2 batteries independently.

SmartShunt
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Kevin Windrem avatar image
Kevin Windrem answered ·

It should work as-is as long as ALL loads and charging sources connect to the system side of the shunt. This includes a chassis connection. That is, the ONLY thing that connects to the battery negative is the battery side of the shunt.

As long as all wiring for the two batteries are the same length, what you have now should work fine. In this case, I'd connect both battery negatives to the shunt rather than jumping between two batteries then on to the shunt. That way, it's easy to keep both path lengths the same.

5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

sheakx avatar image sheakx commented ·

Thanks, That’s what I was hoping to hear. The 3/0 cables to the battery switch are the same length. I read in the install instructions to only connect 1 lead to the battery side of the shunt but using 2 equal length leads makes more sense to me. I also thought I could use both + red wires (one to each battery to view both voltages which should stay the same or very close). Does this make sense?

0 Likes 0 ·
Show more comments
sheakx avatar image
sheakx answered ·

Final update results for anyone reading this thread. The 2 parallel 12V 100AH lithium batteries were wired to the shunt with 2 equal length jumpers. One battery positive was plugged into Vbatt+ and the other battery positive was plugged into Aux and set up like a starter battery. Everything works perfectly.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.