BMV 712 constantly reads about 23 amps but stays at 100% SOC and has 0 consumed AH

The reading on the 712 is not consistent with measured amps at the shunt connections. Have double checked that the shunt is installed before all loads but the current reading stays around 23-24 amps even when big alternator and solar are both producing lots of current, SOC stays at 100% and consumed AH is 0. Have double checked the UTP cable is well connected at both ends. This is on a Lithium bank of 3 relion 300ah batteries. Anything else to help troubleshoot?

BMV Battery Monitor
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Matthias Lange - DE avatar image Matthias Lange - DE ♦ commented ·

Can you please make some pictures of you installation (maybe also a wiring diagram) and screenshots of VictronConnect.

0 Likes 0 ·
crholliday avatar image crholliday Matthias Lange - DE ♦ commented ·

img-1649.pngimg-1650.png

In the pic below the battery side is the left side cable with the loads being on the right. img-1645.jpg

0 Likes 0 ·
img-1645.jpg (73.8 KiB)
img-1650.png (310.5 KiB)
img-1649.png (303.2 KiB)
1 Answer
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

On the second screenshot you have a positive current going into the battery (charging).
The SOC only goes down if you have a negative current going out of the battery.