MultiPlus-II Consumption with no AC Out

I have connected a MultiPlus-II connected

DC

180Ah 48V Batteries

SmartSolar MPPT 250/85

BMV-712 Smart


AC in to Grid

AC out not connected (at this moment) because i just want to feed it.


I configured in ESS to alway kee Batteries charged an a charge limit to 50Watt.


Why is AC Out consuming 35W?

here some more pictures:

Any advice?

Thanks a lot!

Multiplus-II
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Rob Duthie avatar image
Rob Duthie answered ·

Hi

These units are know to self consume and are not very accurate in the the current readings.

So i have being told by the powers that be, just the way it is. As i have a unit with similar self consumption issues.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

dennis avatar image
dennis answered ·

Thanks for your Answer. Maybe it is Firmware related and can be corrected in future.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Rob Duthie avatar image
Rob Duthie answered ·

Hi

One would hope so as the Mulitplus 2 are having issues with ripple relay control signals pulling current when doing nothing can be up 1700watts of power loss when the grid operator

sends the signals down the line to control hot water cylinders etc. in NZ

The frequency is about 350Hz