Fronius Error state 107 - Off grid with Fronius on Output

Hi All.

I have a Fronius Eco on the output of 3x 15kVA Quattro inverters.


PV Inverter assistant is loaded and the GX device picks up the Fronius inverter successfully.

The Fronius give error state 107 - The AC grid outside the allowed limits.


Please assist?


whatsapp-image-2021-05-18-at-151152.jpegwhatsapp-image-2021-05-18-at-151124.jpeg

whatsapp-image-2021-05-18-at-151214.jpeg

Fronius
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

greendovefarms avatar image greendovefarms commented ·

State 107 grid not detected

Are the quattros turned on and running ?

What is the Hz reading for the quattros?

is your wiring correct ? I assume you have the fronius on the output of the Quattros. As you have stated

Are the quattros grid settings correct for an off grid setup? Eg.50hz

I guess the quattros are in 3~ configuration?

Have you measured the quattros output at the fronius where the cables enter the backing plate ?

Do you have any more information about your system ?

0 Likes 0 ·