question

John Thornton avatar image
John Thornton asked

Are there inverter/chargers that are 19" equipment rack mountable?

I am considering replacing a lot of UPS with Victron units. But one of the requirements is the unit must be mountable in a 19 inch equipment rack. Are any Victron inverter/chargers units that form factor?

ups
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

Hi,

You might find this article interesting:

https://www.victronenergy.com/blog/2020/12/07/how-do-you-monitor-a-wisp/

As of the time of this post, there is not specific 19” format models. However the R&D team is aware of the the demand and I expect they will arrive.

They will be on these pages once released,

https://www.victronenergy.com/inverters
https://www.victronenergy.com/markets/telecom

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Kevin Windrem avatar image
Kevin Windrem answered ·

Victron inverter/chargers can function as off-line UPS but lack an important UPS feature: automatic voltage regulation. AVR steps up the voltage going to the loads when incoming AC is lower than a set threshold and steps it down for high incoming AC voltage.

It might be possible to set the incoming AC range small enough to reject the AC input with low/high line voltage but then you would be running off batteries until the voltage came back into range.

Separate chargers and inverters could be combined to form an on-line UPS. Set up this way, the charger and inverter would always be running, which is precisely what happens inside an on-line UPS.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

wkirby avatar image
wkirby answered ·

Although the equipment is not natively 19" format, a couple of us have got creative to mount the equipment in a 19" rack:

https://community.victronenergy.com/articles/86386/my-cabinet-build.html

https://community.victronenergy.com/articles/71664/all-in-one-3-phase-ess-system-cabinet.html


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mvader (Victron Energy) avatar image
mvader (Victron Energy) answered ·

One extra note, all sensitive equipment, such as servers, storage device and other IT equipment, will require an online UPS. Which a Victron is certainly not.


And ofcourse :thumbsup: for replacing things with Victron!

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources

Additional resources still need to be added for this topic