Split Phase Setup in 3 Phase Network

Dear All,

is it possible to create a Split Phase System connected to a 3 Phase network?

First Multiplus 2 connected with AC in on Phase 2 and second Multiplus 2 connected with AC in to Phase 2. ESS with Feed Back enabled.

AC Out only of first Multiplus for some loads used.

All Neutrals connected like it is needed in manual.


Technically it should work, but is it considered by Victron Energy Software?


Thanks a lot!

Multiplus-II3 phase
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
chris-pt avatar image
chris-pt answered ·

Hello, did you try this configuration? It works? I would like to do the same... - Thanks for your return. Chris

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Robert Boerescu avatar image
Robert Boerescu answered ·

vrm2.png

I managed to do it yesterday. So far seems to be working as expected.


vrm2.png (118.4 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Kevin Windrem avatar image
Kevin Windrem answered ·

This was discussed in another thread also. One limitation: the Multis need to be connected to L1 and L2, not L2 and L3. You can see this in the Critical Loads tile above.

2 |3000