Easy solar mppts

Hi.

I have an easy solar 48/5000/70 with the 150/100 mppt.

I.m looking at configuring my panels on a static boat roof.

6 face south, 6 north, and I can place 4 on an east facing roof.

I have noticed the max voltage of these panels on another system reach 50.1 volts, so I can only safely series them in pairs.

Are the 3 pairs of mc4 connectors in the easysolar unit 3 individual and separate mppts, suitable for different aspect strings, or do they all go into just one mppt?

Thanks, Steve.

EasySolar All-in-One
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
JohnC avatar image
JohnC answered ·

Hi @stevla

The 3 pairs of MC4's join together within the unit to one tracker. They exist that way because the MC4 fittings are only rated to 30A and the unit can handle a total of 70A from the pv.

Surprised you can't get 3x in a string, but there's a calculator you can use to check the string suitability.. https://mppt.victronenergy.com/#

Try to keep all your panels of the same specs with so many strings. Having them facing different directions isn't ideal, but should still be ok, especially if you can keep the sun on them all at once.


2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Steve avatar image Steve commented ·

Thanks John.woukd you suggest series 3 on South, and parallel to 3 on North and so on? ..the calculation agrees that I can series 3 up at a time.. cheers Steve.

0 Likes 0 ·
Show more comments
Mike Dorsett avatar image
Mike Dorsett answered ·

you could use a big blocking diode in series with a string of 3 panels, this would give you a 0.45V drop - you lose some power, but it does add some protection. Check the Voc of the modules from the manufacturer's data, and remember to allow for cold operation as the voltage rises when colder than 25C.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

dietrich avatar image
dietrich answered ·

Hi Guys, I've been trying to learn how to make a solar MPPT for battery charging application. I'm still a bit unclear how the MPPT changes the output voltage of the solar panel by varying the duty cycle. Can anyone shed some light on this for me? :)