Has anyone seen this before where ESS drains the batteries into the grid?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Has anyone seen this before where ESS drains the batteries into the grid?
We need more information about your system and maybe some screenshots of your settings (Venus and VE.config).
Hi @Netrange
Please don't draw conclusions too fast from a single topic, I think that was related to something else.
Helo Daniël Boekel,
does Victron have an Idea why this could happen?
Or is it even a Feature?
I believe it's an ESS Problem under certain conditions.
The BMS from the BYD Lithium Battery was functioning correctly.
I would appreciate it to have an Statement of the Professionals....
Thanks in Advance
Peter
Dear All, interesting. Yes this happens in my system too.. Not every day.. sometimes.. This can not be seen on the VRM, as this happens only for a few seconds. Have seen this happening only when the battery still need to be charged.
The system I have is small: Multi 12/800/35 MPPT100/50 2xPV 280Wp and a 60Ah Lithium LifePO4(Smart Victron). ESS = Optimized(with BatteryLife) Minimum SOC 65% GridSet point 50Watt
Regards, Rob
Hi,
system is 2 x multi 48/5000/70 in parallel, 800Ahr VRLA, 2 x SMA solar inverters, color controller firmware 2.66.
ESS Optimised(with BatteryLife), Minimum SOC=80%.
System has been running for around 5 years fine and this problem started about 8 months ago. To solve it I move ESS to “Keep Batteries Charged” but then I cannot take advantage of the batteries unless grid fails.
Your ESS Minimum SoC is set to 80%.
If you want to be able to use the top 20% of the batteries to support non-essential loads (upstream of the inverter), but not feed into the grid, then add an energy meter eg. ET112 or ET340.
If the inverter loads are all you want batteries to support with ESS, then just disable DC-coupled Feed-in in the ESS menu.
(Previous version of this answer included the following incorrect statement:
If you have DC-coupled feed-in enabled, ESS will discharge your batteries into the grid until 80%.)
Problem is not PV related as the discharge happens day and night. It discharges to SOC then recharges to 3% above SOC then cycles this continuously
Please see my answer below.
If your minimum SoC is set to 80%, ESS will discharge the top 20% into the grid. That is what it is designed to do.
Hi,
i had the same Problem.
For 1.5 Houers the ESS draind the Battery to 20% :-(
Happend already once before.
Fronius, Color Contol, Quattro, BYD Battery, Energymeter....
Does anybody know, why this happens?
Peter
yes something is not right here as my system also has erratic behavior in the "feedback into grid" which - by using a grid code should not be allowed
Is the status of vrm "realtime"? If not (and I can't see from this screenshot) then the data could be inaccurate. Do you have energy meters and how are they configured - since "AC loads" is shown you must have a meter on that side and "AC output" enabled.
Perhaps rather open your own thread and clearly document your components and settings, since your issue is something else unrelated to this topic.
Looks like something is misconfigured.
Your grid set point should be set to 0W then on your selection screen de select AC coupled feed in excess as your image shows a DC coupled PV Charge so you should have that selected and limit the feed in to just under the max of the PV charger or just set it to zero if you don't want to feed back
the meter needs to be on the AC input side to be able to manage grid power and feed in
Try this first a I had a similar experience and tried setting the grid set point to all sorts of values ie if -50W dc feed back to the grid if 50W it would start charging the battery from the grid although only a small amount
Hi, was there any solution to the battery discharging into the grid? We have a site experiencing the same thing.
I have the same problem where my battery is being drained into the grid.
I have a simple system (25kWh battery, 3x5kVA Multiplus-II inverters, 3x MPPT with 15kW solar panels).
Even at night, I occasionally will find my batteries being drained into the grid when there should not be any need for it. I've tweaked the Grid SetPoint anything between 0 and 400W but that does not seem to fix this permanently. The ESS assistant baffles me sometimes. I really want to use it, but these types of issues make it difficult, as I'm actually paying for energy being fed back into the grid (using a pre-paid electricity meter that always counts one way).
Similarly, the constant bits of energy being fed back to grid as it's trying to equalize is frustrating - sometimes it will take 10 minutes for the grid value to show a positive number after loads change.
Any insight from Victron staff would be greatly appreciated.
Thanks