MPPT 100/20 FUSE

Hi everyone. I have SmartSolar MPPT 100/20. And I have two questions: should I put a fuse between the controller and the battery? I know that there is already a 25A fuse in the device, but I do not know which line is protected by PV - MPPT or MPPT - BATTERY or maybe both or just LOAD? And second, is it true that if I disconnect the battery with solar panels connected, I will damage the charge controller? Regards Chris

MPPT SmartSolar
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
seb71 avatar image
seb71 answered ·
should I put a fuse between the controller and the battery?

Yes. Size it to protect the wire.

is it true that if I disconnect the battery with solar panels connected, I will damage the charge controller?

You should avoid doing this. The charger might be damaged (so this "might be damaged" means that it can also might be fine).

5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kdrozda avatar image kdrozda commented ·

Thanks for the answer, can you tell me what fuse value ... 30A?

0 Likes 0 ·
seb71 avatar image seb71 kdrozda commented ·

What wire size (cross section) you will use betwen the battery and the MPPT charger?

0 Likes 0 ·
kdrozda avatar image kdrozda seb71 commented ·

6mm2

0 Likes 0 ·
seb71 avatar image seb71 kdrozda commented ·

That's the maximum it can take, right?

And I assume it's copper.

Use a 25A fuse.

0 Likes 0 ·