Is this a vrm bug or am I sending something incorrect with my tank sensor

Im working on a modbus to dbus tank sender interface

I have the /Remaining reading ok on the unit (ok incorrect units as well) but on vrm it displays with an additional 3 zeros after it on the graph . see graph below

1620289875119.png

1620290068153.png

1620291029135.png

Thanks

D

VRM
1620289875119.png (46.3 KiB)
1620290068153.png (2.5 KiB)
1620291029135.png (26.5 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Kevin Windrem avatar image
Kevin Windrem answered ·

I would look at the way the dBus parameters are created. The /Remaining parameter is a value between 0 and 100 representing the tank's level as a percentage. I think the parameter is normally created as an integer although my TankRepeater makes no specific type declaration when creating it's dBus services.

If you create the parameter as a float, then VRM may be doing the right thing. I'd make sure the add_path call doesn't have a decimal value for initial level.