Hi,
what does "Max AC current 100% of INom" stand for in the VE configure?
Missing information in the help system.
Maybe someone has detailed information on this.
Sunny regards
Thomas
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hi,
what does "Max AC current 100% of INom" stand for in the VE configure?
Missing information in the help system.
Maybe someone has detailed information on this.
Sunny regards
Thomas
I had the exact same question today and also couldn't find any documentation about this. What I was looking for was some way to limit the maximum AC current, that can go back into the grid when using the ESS. I am aware that there is an option for the ESS to limit the inverter power. But this is no hard limit and can be exceeded for many seconds until it slowly regulates the power output. Since this was no option for my scenario I took the risk and tried the "Max AC current of Inom" option.
If you hover your cursor over the input field, it tells you for the MP2 48|3000 model that Inom is 11.08A. So I tried different values and got the following measurements on the AC-in:
100% -> ~11A
75% -> ~8A
50% -> ~5A
...
You see where this goes... So it seems to do exactly this. Limit the current that can be feed into the grid. This also seems to be a "hard limit" that is never exceeded. I will keep an eye on it over the next days to be sure it is really doing what I am expecting.
Keep in mind that you need the "grid code password" to change this value.
Settings -> ESS -> NetFeeding -> Max Feed
Maybe menu entrys are translated wrong because my settings are in German. But you can configure when and how much of the Excess go to the grid there.