Hi!
I'm building a new setup for a 24V system with Multiplus II for solar and wind. The battery system is flooded lead acid and I'm interested in monitoring the battery level and charge rate with a Cerbo GX. My question is about the following busbar setup I'm currently planning:
Left side: Lynx Power-In (4 IO slots)
1/ 24V battery system
Right side: Lynx Distributor (4 fused IO slots)
1/ Multiplus II 24V 3000VA
2/ Solar charge controller
3/ Wind charge controller
4/ Victron non-isolated DC-DC converter 24V->12V
It would be elegant to add a Lynx Shunt V.E. Can in the middle, but it would be quite expensive and the CNN-type fuse is crazy expensive. So my idea is to add a 500A SmartShunt between between lower negative bus and then a wire/plate between the upper positive bus. (On a side note, if the Distributor had 5 slots, I could only use that and put the shunt on the negative battery cable.)
Is there anything wrong with this setup for the intended purpose? Do I still need a separate fuse for the battery side?