I just want to be sure that I am getting this right. When running the AC in or out wires my inverter will be 32 feet from the breaker panel/box. Will 6/3 wire be enough for that length?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
I just want to be sure that I am getting this right. When running the AC in or out wires my inverter will be 32 feet from the breaker panel/box. Will 6/3 wire be enough for that length?
Hi @rporcoro, yes, 6/3 will be more than sufficient for that - 6AWG can carry 120A continuous safely, and at 120VAC you'll only experience roughly a 0.53% voltage drop over the course of that run.
The wire type significantly affects ampacity. The chart I found specs #6 for 55 amps at 60 degrees C (e.g., NM-B (romex)) and 65 amps at 75 C (THWN or SO), and one for "marine" wire is rated for 120 amps at 105 C outside engine space or 102 amps inside the engine space.
The AC in on a Multi 3000/120 is rated for 50 amps, but the AC out can benefit from power assist for an additional 3000 VA (25 amps). So the total for both AC 1 and 2 out could be up to 75 amps with full shore power and power assist. You'd want to limit the output current with a circuit breaker for the wire type you end up using. (AC 2 out is limited to 25 amps.)