Can I connect a 12V load to the Smartsolar 100/20 in a 24V system?

I am asking the question in advance of actually having set up try out of curiosity. I am wandering if I can connect a 12v load while the MPPT unit is charging battery bank at 24v?

My guess is no as figure once a system voltage has been chosen by the controller all functions will be set such.

Interested to hear thoughts though as may well be another little bit of magic Victron smart controllers seam to be able to perform.

MultiPlus Quattro Inverter Charger
7 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

klim8skeptic avatar image klim8skeptic ♦ commented ·

The battery and load terminals are 24v.

WHERE do you think you can get 12v?

0 Likes 0 ·
jamesinwa avatar image jamesinwa klim8skeptic ♦ commented ·

As I said simply a thought. YOU simply confirm MY logical conclusion To my OWN question.

A curiosity was the basis of the thought. IS the natural progression that multi v range units progress toward.


To treat your WHERE seriously wold be the unit already contains circuitry to auto detect 12/24 voltage would simply require a buck/ boost component to allow the unit to deal with both its capabilities individually.

0 Likes 0 ·
klim8skeptic avatar image klim8skeptic ♦ jamesinwa commented ·

Your Mppt will auto detect battery voltage (or manual selection) and charge battery voltage appropriately.

0 Likes 0 ·
Show more comments
wkirby avatar image wkirby ♦♦ jamesinwa commented ·

The Load terminals are simply switched to the Battery terminals with a current sensor included also. So all loads will need to be the same Voltage as the system battery Voltage.

There isn't room inside the MPPT for another DC/DC converter.
In most cases, people need the Load Output Voltage to be the same as the battery Voltage, so a built in DC/DC would be wasted.
If you do need Voltage conversion then you'd need to use a separate DC/DC converter. There are a selection of Victron ones available to suit your needs.

0 Likes 0 ·
Show more comments
2 Answers
ceriw avatar image
ceriw answered ·

no, you would need a separate DC-DC converter

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jamesinwa avatar image jamesinwa commented ·

anything that alters the voltage after it leaves the load output works

Be it an inverter, dc-dc or simple buck/boost circuit

0 Likes 0 ·
jamesinwa avatar image
jamesinwa answered ·

Yes makes perfect commercial sense not to include the circuitry in a single product when is a separate unit sold to perform such :)

Just joined the forum as stated in the opening post is more along the lines of what can be that what is.

A basic step down would suffice on the load output but hopefully as unit development progresses such will not be required. once a nit has multi voltage capability how it manages such is already present.