Hi, can anyone explain max current the Multi is capable to transfer. The manual says:
I have opened the Multiplus case and I see only 32 Amps relays there:
From the photos above you can see there are only 32Amps relays. I think the relays will blow up in the case the Multi will add its 13 Amps to the 32Amps on AC-In.
Is the manual stating wrong numbers? I have searched the specs of the relays and it seems they are not able to handle 45 A even for short period of time.
Can someone explain why the 32 relay is used when Victron declares that it should handle max 45 Ams? How to size the circuit breaker here? I think 32A circuit breaker should be enough in the case 32 Amps relays are used internally by Multi.