MPPT 250/100 Tr Maximum 390W panels

Obviously a newby here, I have 28 390 W Canadian solar panels and would like to know if I can connect them to my smart solar MPPT 250/100 in 7 strings of 4 connected in series.

The Isc is 10.17 A

Voc 48,2 V

MPPT SmartSolar
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
JohnC avatar image
JohnC answered ·

Hi @jumboswart

The maximum string Isc for the 250/100 is 70 A, so 7x strings would exceed that. 6x would be ok.

Consider 4x of those strings into the 250/100, and adding a 250/85 for the other 3x strings. That would be a far better match at charging V's.

I'm all for having extra panels to allow for bad weather, but that's a lot of panels on a single mppt..

7 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Hannes Swart avatar image Hannes Swart commented ·

I didnt mention that I also have a SmartSolar MPPT 150/100, could I then say put 4 strings on the 250/100 and 3 on the 150/100?

0 Likes 0 ·
Show more comments
Hannes Swart avatar image Hannes Swart commented ·

I was trying my luck to get away with using just 1 mppt

0 Likes 0 ·
Show more comments
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

https://www.victronenergy.com/mppt-calculator

https://www.victronenergy.com/upload/software/VE-MPPT-Calc-4_0.xlsm

An important thing to know is the battery voltage.

The 250/100 can charge the battery with up to 100A -> 1200W at 12V, 2400W at 24V and 4800W at 48V

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Hannes Swart avatar image Hannes Swart commented ·

I have a freedom won 30/24 lipo4 battery with a nominal voltage of 52 V, min 47 V, max 56 V

0 Likes 0 ·