soe15 avatar image
soe15 asked
ESS + 3 BMZ batteries, system is not discharging at night
I've got a ESS with 3 BMZ batteries (364Ah), MultiPlus 3000/48V, Venus, ET340 together with SMA Tripower 20.
Latest firmware on MultiPlus and Venus.
ESS Assistant on MultiPlus acc documentation for BMZ.
System is charging with PV surplus but not discharging, see below.
I tried a lot already incl. reconfiguring Multi, exchanging the Venus with a CC, but no change.
Does anyone has an idea?
Thanks, Stefan
ESS
boekel avatar image
boekel answered ·
What does 'Konst.-Strom' mean in English?
can you make a schreenshot of the ESS settings?
soe15 avatar image
soe15 answered ·
Hello Boekel,
thanks,
Konst.Strom means constant current
06048CFE
boekel avatar image boekel ♦ commented ·
Ok. I'm out of ideas for now... what could give some hints to other users here or Victron staff is also posting screenshots of the settings in the Multi's.
If you set gridpoint to something like -200W, does it discharge into the grid?
soe15 avatar image
soe15 answered ·
Its solved now.
There was a Smart1 Energymanager in the same network that tried to connect to the Venus via Modbus. Although Modbus was disabled on the Venus, it was disturbing the ESS functionality.