Victon Lithium - first charge - results at end of absorption

Hi All

Just charged a bank of 3 lithium 200Ah batteries (in parallel - total 600Ah) - for first time.

Set the charger to be in absorption for 2 hours - as per manual.

See pictures showing BMV and the 3 batteries - these screen shots were taken 2 minutes before end of absorption (2 hours). I was expecting to see all batteries at 14.20 - but they are all below this.

Does this look OK ?

Thanks

Tim

2021-04-25-135351.png2021-04-25-135403.png2021-04-25-135413.png2021-04-25-135448.png

battery chargingLithium Battery
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
seb71 avatar image
seb71 answered ·

The cell voltages look OK, especially if it's first time you are charging the batteries.

How are the batteries wired in parallel? With or without busbars?

7 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

miya avatar image miya commented ·

Thanks Seb71

Wired in parallel - all wires same length - all +ve and -ve going to a Victron Lynx Power-In.

0 Likes 0 ·
seb71 avatar image seb71 miya commented ·

That's good.


How many Amps during Bulk stage you charged with?


0 Likes 0 ·
miya avatar image miya seb71 commented ·

Started the multiplus at a very low 10A after installing the VE.Bus BMS Assistant. Then increased to 20A after about 10 minutes - then increased to 30A after another 5 minutes - and left it there (30A) for remainder of charge.

In total the batteries spent about 4 hours in bulk at 30A. Then - 2 hours in absorption.

0 Likes 0 ·
seb71 avatar image seb71 miya commented ·

30A is low for your 600Ah battery bank. Very slow charging.

0 Likes 0 ·
miya avatar image miya seb71 commented ·

Yes - I will increase settings in Multiplus to much higher - when I use in anger.

I left it at (low) 30A during this first charge - as I was watching the V rise steadily - in just 4 hours it left bulk and went to absorption. My logic is 4hours x 30A = 120A was pushed in to 600Ah bank - which is only 40A per battery = which indicated the batteries came about 80% full from factory.

Sound about right to you ? Or, do you think the batteries have not charged fully - my original worry ? On delivery the batteries were showing 13.28v (3.32v per cell).

0 Likes 0 ·