question

marekp avatar image
marekp asked

MP-II jumps SOC value from 20% to 100% when 2 signal BMS said "do not charge"

Hi,

My 3 phase system build on 6 x MP-II/3000 uses Lithium battery with BMS that connects to the system through 2 signals (4 wires). One signal is for preventing charging the other discharging.

ESS assistant has "2 signal BMS" selected.

Recently I had a situation when battery was discharged down to 20% and BMS sent the signal "charging not allowed". As a result MP-II set the SOC of the battery to 100% and charging mode to float. In reality, the battery was practically discharged.

The reason the signal was sent, was not that the battery was full (obviously), but temperature of one cell dropped below 5C.

Does anyone have a solution to this problem?

Regards,

Marek

screen-shot-2021-04-24-at-31009-pm.png


bms-tmin-error.jpg

Multiplus-IIBMS
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

marekp avatar image marekp commented ·

Hi,

Do anyone have any suggestion how to deal with this problem?

This morning again MP-II set the SOC to 100% but my BMS reports SOC at 17%.

Again minimum battery temperature at 6AM fell below 5C.

0 Likes 0 ·
1 Answer
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

There is an option during the setup of the two-signal-BMS assistant. "Set SOC to 100% if cell is high" or something like that.

7 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

marekp avatar image marekp commented ·

Hi @Matthias Lange - DE,

I do not remember seeing this during the ESS setup.

There is "force to Float when BMS signals battery full...."

This is not saying that the SOC will be set to 100% but maybe "Float" is synonymous to SOC=100%.

But this signal from BMS was not about battery being full but the temperature of the battery was below Tmin=5C.

When I turn of this "force to Float..." option, what will happen when battery will get to full charged state and BMS would send the signal "do not charge"?

Do you know of any other way to get battery's SOC, that would not react to the BMS's signals?

Regards,

Marek

l1-m-ess.jpg

0 Likes 0 ·
l1-m-ess.jpg (150.6 KiB)
Matthias Lange - DE avatar image Matthias Lange - DE ♦ marekp commented ·

OK, this option don't appear in the ESS assistant only in the two-signal BMS assistant.
two-signal-bms.jpg

1619281716148.png

Do you get a SOC signal from the battery or do you use the internal battery monitor of the Multi?

0 Likes 0 ·
two-signal-bms.jpg (145.0 KiB)
1619281716148.png (9.7 KiB)
marekp avatar image marekp Matthias Lange - DE ♦ commented ·

Hi @Matthias Lange - DE,

Thank you for your input.

If this option is not available in ESS assistant, than what I am to do with this problem?

ESS assistant does not allow the "2 signal BMS" assistant loaded.

My BMS has only two dry contacts.

One for "allow to charge" and second for "allow to discharge" and each of them has two reasons for happening.

First indicates that the battery is charged (one cell reached a highest voltage allowed) or temperature of the cell is below the T1min or above Tmax.

Second indicates that the battery is discharged (one cell reached the lowest voltage allowed) or the temperature of the cell is below the T2min or above Tmax.

(T1min is a minimal temperature for charging)

(T2min is a minimal temperature for discharging)

There is no SOC information send to MP-II from this BMS.

The SOC state is "controlled" by a MP-II.

I am willing to buy an external device (smart shunt maybe) to keep track of SOC of my battery but I need to be sure that it will not be just another additional expense and the problem will remain. (just like buying power meter for my PV inverter)

Regards,

Marek

0 Likes 0 ·
Show more comments