BMV 712 to inverter connection

I have a bmv 712 with 500a shunt. Can I connect the negative cable of my 2000w inverter to the shunt to measure usage?

BMV Battery MonitorPhoenix Inverter
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Alexandra avatar image
Alexandra answered ·

@Benodonohue

Yes you can. I am assuming you have a 12v system. A basic calculation example below. If it is 24v the system amperage draw is half so even less of a load on the shunt.

12v x 500A is 6000W - your 2000 watts even at 100% overload will not max it out in any way.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

benodonohue avatar image benodonohue commented ·

Yes it’s a 12v system, Thanks,

0 Likes 0 ·
damn-electricity avatar image
damn-electricity answered ·

Hi, did you manage to fix that. My phoenix inverter is just arrived, causing the same question.


Many thanks,

Thomas

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kevgermany avatar image kevgermany ♦♦ commented ·
Same answer, yes, as long as it's the DC negative.