Hi there

I note in the manual for the Smart BMS Cl 12/100 that the Multiplus 3kva must be of 'recent type' with auxillary inputs. I bought my Multiplus 12/3000/120 about 6 months ago. Can anyone tell me if this version is compatible, picture below of the inputs on my unit.


Thanks


20210415-202146.jpg


MultiPlus Quattro Inverter ChargerBMSve.bus bms
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
tozz avatar image
tozz answered ·

The manual states: "Application example with a 3kVA Multi of a recent type that has auxiliary inputs". Judging from your photo, you have 2 aux inputs. So even while your unit seems to be from 2017, with hardware revision 1 it looks 'new enough'.


1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Matthias Lange - DE avatar image Matthias Lange - DE ♦ commented ·
So even while your unit seems to be from 2017,

The serial number starts with HQ2045 so that unit is around 6 months old. ;)

0 Likes 0 ·
tozz avatar image
tozz answered ·

Also, when I lookup the manual for the MultiPlus, the connection overview in the latest manual is identical to your photo. So it looks like you are good to go!

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

daveybdublin avatar image daveybdublin commented ·