I have a 15KVA Quattro running ESS Assistant and set to use 60% of battery capacity for self consumption (Optimised without battery life).
I am looking to switch off/disconnect the AC output at 30% SoC in case of grid failure/load shedding/poor quality mains supply using assistants ( I understand from the ESS manual that the settings in the Ve Configure 'Inverter' tab for DC low voltage shutdown and shutdown on SoC are completely ignored while running ESS.
In the VeConfigure assistants page, I have set after the ESS assistant;
1) Programmable Relay (Drive on SoC), set 'Primary Programmable Relay' ON when SoC at 30%
2) Safety switch assistant set to switch off when the Aux 1 relay is set to ON.
3) Programmable Relay (Drive on SoC) to set Aux 1 back to OFF when SOC at 35%
I have written the assistants but nothing happens when SoC gets to 30%, the inverter keeps going and drains the battery beyond my desired setpoint.
I understand there is some additional physical wiring to be done for the safety switch to work - I have three questions.
1) Are the Primary Programmable Relay and Auxilliary Input 1 thesame?
2) If they are thesame is it safe to short the + and - on the Auxilliary input 1 without damaging the inverter?
3) Can anyone please help identify the specific physical contacts/safety switch connection points to use on a 15KVA Quattro and how to wire it up correctly?