900 Amp House Main Battery Bank. How many Multiplus Chargers are needed

I am looking to install 4 Northstar SMS AGM 480 batteries giving me 868 Ah of total capacity. I been reading a couple of article on sizing but thought I would ask this community to weigh in.

868 Ah

868Ah * 10% = 86.8Ah.

868Ah * 20% = 173.6Ah

Even though the 20% value is outside the MultiPlus 12/3000/120. I would like to get your opinion on whether one or two MultiPlus 12/2000/120 units are needed. I also have a Northern Lights 6K generator and no solar at this time.

Thank you in advance.

MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
seb71 avatar image
seb71 answered ·

Consider a 48V system instead.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Kevin Windrem avatar image
Kevin Windrem answered ·

It all depends on how fast you want the batteries to recover. It would take the Multi 3000 about 4 hours to move the batteries from 50% to 100% (900/120).

If the Multi 3000 provides enough AC output, a less expensive way to add more charging capacity may be to add a just a charger.

I would agree with seb71 that a higher DC voltage should be considered. There is no 48 volt Multi 3000 for 120 volts. 24 cuts currents in half. You would also benefit from about 16% faster charging.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

The rule of thumb says a lead/gel/AGM battery should be changed with a current that is 10-15% of the capacity.

So for your battery pack 86.8-130.2A. That means you are perfectly fine with one MultiPlus 12/3000/120.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.